Indirects and ASME, what do y'all find in your area
tim smith
Member Posts: 2,807
for asme is 5 cubic feet or 33 gals tank size so rarely do we exceed this or we just do 2 tanks to minimize size.
0
Comments
-
Indirects and ASME, what do y'all find in your area
Just wondering what you all are seeing w/ inspectors on this subject regarding boilers over 200mbh and indirects. We are finding that our local regulators are requiring asme on indirects when boilers are over 200mbh and connected to a indirect. early 08 we went through this and they said we could use an indirect w/ out asme if the rating on the indirect showed it was not transferring more than 199,999 btu but now the official is saying he will not look at the transfer rate, just btu of boiler!!!! Frrrrrustrating. Any input say you all. Thanks, Tim0 -
Expansion tank
Is he looking at your expansion tank rating as well?
0 -
Turbo max
I beleive that Turbomax makes an indirect that is asme. They are a bit pricy so if you get a price let the supplier know it has to be ASME.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
ASME
Turbomax does offer ASME versions but only in the larger models. T65 (up to 500K btu) an T109 (up to 1 mil btu)
Are you seeing this only in Commercial applications or in residential as well?0 -
In Seattle, both res & comm. I have seen the reverse indirects
from turbomax but I still like the Superstore stainless tanks. They have treated us well but as I said, the city is putting the screws on these even though they show they don't exchange more than 200mbh.. Oh well, back to the drawing board. Thanks, Tim0 -
In Colorado...
they look at the transfer rate, with the tank at 180, and the boiler at 200, and without the delta T, it won't transfer 200K...
It is quite easy to misinterpret the code...
METhere was an error rendering this rich post.
0 -
Mark, the problem with the code is they do not directly say
that it is the transfer rate, they also say it is up to the local code/jurisdiction authority to make their decision. If they said transfer/transmission rate in the ASME code I think our official would buy off but nooooooo. Tim0 -
The reason for the ASME requirement can be found in ASME sec IV part HLW -101.2. This sec. states that water heaters are exempt when none of the following are exceeded
input: 200,000 btu/hr
water temp. 210 degrees
capacity 120 gal.
The Washington boiler board is looking at this so the requirements may change. The city if seattle must meet all state jurisdictional requirements, however they can exceed the requirements if the choose.
the current jurisdictional code book can be viewed on the lni web site
look @ the definition for hot water heater
RCW 70.79.080 (12)
RCW 70.79.090 (5)
www.lni.wa.gov/tradeslicensing/boilers
The city of Seattle boiler sec. will be hosting a stackholders meeting in the near future to discuss this and other changes. check the jurisdiction and Seattle web pages for information.
hope this helps0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements