Weil-McLain Ultra Venting Length
Pat_30
Member Posts: 1
What is the maximum vent length for a Ultra 80? The table in their manual says a Max of 100' with 2 elbows. Is this the total for just the flue pipe? Or is it the total for the flue and fresh air intake combined?
No, you get a 100 feet w/ 2 elbows and for each addl 3\" long
radius elbow you will deduct 7ft from the length allowed. Kapiche. Tim
Ps, no idea if Kapiche spelled that way but sounds good.
Kapiche
Kapiche i think is Italian?
In German it is Kapieren or: do you Understand in English.0 -
and make sure your pitch is correct
specifically, no sags that can create condensate 'traps'0 -
100' for each