Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

water radiator into steam radiator

Options
Jim_64
Jim_64 Member Posts: 253
hi,
Im changing radiators, i just converted a water in steam. i noticed the opening where i attached the on/off valve is 1.5 inches, however my on/off valve is 1 1/4 inches. how can this be adjusted?

Comments

  • Kool Rod
    Kool Rod Member Posts: 175
    Options


    Generally one would use a 1 1/2" x 1 1/4" reducer bushing.
    I'm assuming the "opening" is the "hole" at the bottom end of the radiator. Just don't do the reducing on the intake line as this could cause water hammer.
This discussion has been closed.