water radiator into steam radiator

Jim_64
Jim_64 Member Posts: 253
hi,
Im changing radiators, i just converted a water in steam. i noticed the opening where i attached the on/off valve is 1.5 inches, however my on/off valve is 1 1/4 inches. how can this be adjusted?

Comments

  • Kool Rod
    Kool Rod Member Posts: 175


    Generally one would use a 1 1/2" x 1 1/4" reducer bushing.
    I'm assuming the "opening" is the "hole" at the bottom end of the radiator. Just don't do the reducing on the intake line as this could cause water hammer.