steam system short cycling. Can I replace a vacuum breaker wit
Options
mike cipollone_2
Member Posts: 7
Dear Wall, This system cycles every 3-4 minutes from a cold start on Vaporstat. There are two vacuum breakers on the last part of the return within 5 feet of boiler. As soon as I remove the vacuum breakers, the unit ran without stopping. Can I replace the vacuum breakers with end of main vents? Mike Cipollone
0
Comments
-
Of course
those vac-breakers let air in, but not out! The air has to get out so the steam will distribute.
Is this a one-pipe or two-pipe system? The answer will help us determine what vents to use.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Steamhead, Hello, we met at The Eastern State Penitentiary last year with Dan. It is a two pipe system. Thanks, Mike0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements