TT-110 run time
Eileen Olive
Member Posts: 99
Just want to check the running of my new TT-110. Tonight it is 28* outside. The boiler fired and ran for about 45 minutes, at what sounded like high fire, ending with Supply of 146* Return of 126*. It then shifted to read 6-132 Supply and 6-128* Return, and sounded as if it were shutting off. But it then started up again but at a much lower firing rate, reading 3-136*Supply and Return 120* and ran for another 20 minutes at this reduced firing rate. So for a total time, the boiler ran for 1 hour. generally it will not fire up again for apx 3 hours. How does this sound?
0
Comments
-
TT
The "6" means its reached the temp required(for in/out if used) and the burner has stopped.
The "3" means the burner is firing(modulating) attempting to maintain the required water temp.
Do you have your proper temps dialed in?
Dave0 -
Do not know
I am using the factory-set parameters. I do not know exactly what the setting should be.0 -
Here`s a
good thread for TT 110 settings by UniR.
If your inclined to deviate from factory settings, this should help.
http://forums.invision.net/Thread.cfm?CFApp=2&&Message_ID=435227&_#Message435227
Dave0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements