Water Gauge on Boiler
BRIANJ
Member Posts: 118
Homeowner here who has had a similar problem with my Peerless boiler. I presume when you say water gauge you mean sight glass. Before you do anything check that the valves at the top and bottom of the sight glass are open. If this clears the sight glass you're done.
If you're handy and very careful you can clear up the problem.
Let the boiler cool off to room temperature and drain. Close the top and bottom valves on the sight glass. Remove the two brass bars that protect the glass and carefully unscrew the fittings at the top and bottom of the tube. Remove the sight glass.
If there is crud in the bottom valve, you will probably have to remove the valve to clean the port properly. Have a bucket handy to catch any remaining water and crud. A bottle brush works well to clean the port. You may want to repeat the same procedure on the top port just to be sure it's clear.
You say the boiler was cleaned last year. Do you mean skimed? This process will remove oils and some dirt from the manufacturing process but will not remove all the crud from the bottom of the boiler. If you have an old system and the problem occurs again you should call in a pro to clean the returns.
Just my $0.02.
If you're handy and very careful you can clear up the problem.
Let the boiler cool off to room temperature and drain. Close the top and bottom valves on the sight glass. Remove the two brass bars that protect the glass and carefully unscrew the fittings at the top and bottom of the tube. Remove the sight glass.
If there is crud in the bottom valve, you will probably have to remove the valve to clean the port properly. Have a bucket handy to catch any remaining water and crud. A bottle brush works well to clean the port. You may want to repeat the same procedure on the top port just to be sure it's clear.
You say the boiler was cleaned last year. Do you mean skimed? This process will remove oils and some dirt from the manufacturing process but will not remove all the crud from the bottom of the boiler. If you have an old system and the problem occurs again you should call in a pro to clean the returns.
Just my $0.02.
0
Comments
-
Water Gauge on Boiler
I've been having a problem with the water gauge on my Peerless Boiler. The gauge remains full and I can't drain it. I know the boiler is not flooded because when I remove a bucket of water the low water warning comes on. I'm thinking It's sludge build up and its not allowing water flow in and out the the gauge? I had the Boiler cleaned last year, so I'm a little stumped. Any thoughts?
Thanks,
Travis0 -
either that or one of the valves is closed off....take the glass out and spin out the valves, they can be cleaned but for the cost of new harware it might be worth it to just go out and buy all new before taking anything apart...this of course is speculation on how old the existing parts and pieces are0 -
The unit is new. It's only 4 years old. Is it difficult to clean out the valves or is this something a pro should handle?0 -
Are you sure that
it is not a liquid-filled gauge?
Some are filled with mineral oil or glycerin as a dampener to avoid shock. There usually is a small bubble of air near the top for expansion.
Does the gauge respond reliably to pressure? Go to zero when the boiler is off and cold?
I have to ask.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements