B-Vent that sweats
Scott383
Member Posts: 4
The unit is draft induced so there is no draft hood.
B-Vent
I have a Boiler that is 80% ant the inside of the B-Vent is sweating. Any idea as to what it could be?0 -
Sweating, silly....
I would think that your flue pipe is simply below your apparatus dew point. What is the ambient temperature around the B-vent?
Also, where is this relative to dilution (draft hood)?0 -
Dilution is the solution to pollution...
and producin condensation...
When it happens to us, we block of the draft hood and install a barometric damper, and the problem goes away.
ME0 -
Condensation
Also-you could be returning water to the boiler that is too cool and causing the flue products to condense-80% Boilers require return water temperatures 140 or above0 -
My return temp is only about 120. This must be the problem. Thank you to everyone for your help.0 -
Vent Size
Your vent may be too big, as well. Vent tables for fan-assisted units show minimum BTU/hr requirements. If the vent pipe is too large, you will condense inside.0
- 87.4K THE MAIN WALL