flange joint problem
Options
nicholas bonham-carter
Member Posts: 8,578
after our new 1-pipe steam boiler installation, when our original pressuretrol was set down as low as it could go; it failed and allowed the pressure to rise up to the cut-out reset point[10 psi ].
this over strained a couple of old flange-joint gaskets, which were then replaced. the nuts and bolts were replaced with next size smaller [all he had in his box]. this allowed the joint to rotate slightly, changing the pitch of the upstream pipe causing a pooling of condensate to reduce the steam flow to 1 radiator.
it took a bit of head-scratching to figure out the solution to the problem. so always check the pipe pitch when repairing a flange-joint! maybe the maximum pressure should be set down to 2 psi before starting the boiler for the first time.--nbc
this over strained a couple of old flange-joint gaskets, which were then replaced. the nuts and bolts were replaced with next size smaller [all he had in his box]. this allowed the joint to rotate slightly, changing the pitch of the upstream pipe causing a pooling of condensate to reduce the steam flow to 1 radiator.
it took a bit of head-scratching to figure out the solution to the problem. so always check the pipe pitch when repairing a flange-joint! maybe the maximum pressure should be set down to 2 psi before starting the boiler for the first time.--nbc
0
Comments
-
What size
flanges were they ? That's alot of rotation to change the pitch of a pipe .
We've been having some problems with new pressuretrols also . We don't set the main dial lower than 3 now ( diff is subtractive ) , otherwise you're temping a callback for no heat . I'm suprised yours failed in the closed position . Did you turn the screw so far down it popped out of the spring ?0 -
mexico
EVER since the pressuretrols started to be assembled in mexico the trouble began . before that ....never a problem. if a mechanic does not know how to work on flanges properly he should not touch them. working on a steam line & not checking pitch w/ a level indicates wrong man for the job.0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements