Whistling rad vents
Stewy_2
Member Posts: 83
My rad vents have been whistling quite a bit lately. Also when the boiler kicks off lots of air is released from the vents. The two 2" 10' mains are running two each #1 Gortons. Anybody have any words of wisdom?
0
Comments
-
Boiler Kicking Off
Could it be that the air is rushing into the valve when the boiler cycles off? This happens to me, and I thought it was air leaving the valve, but it actually is air entering the valve. When the boiler cycles off, a vacuum is created and air rushes into the valve. I believe this is normal. As for the whistling, I can't offer any help there. I have the same problem, and others have suggested that it is because of insufficient venting of the main.0 -
whistlers mother
if you find the vents whistling on burner shutdown, it is a sign that the main vents are not handling the relief of the vacuum in those pipes adequately, and therefore, the poor radiator vents are working much harder than they should [but whistling as they work!]
you could try taking the main vents off [boiler-off!] and giving them a soak in dish-washing liquid, with a follow-up of a 1-hour vinegar bath to remove any dirt or calcium obstructing the passageways. alternatively it might be time for new main vents, and my take on the situation is they can never be too big!--nbc0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements