Usin a Taco ZVC406EXP

john p_2
john p_2 Member Posts: 367
Have one left over zone on myTaco zone control panel and want to know if I could use it to power the fans on two hot water unit heaters in my garage. I already ran stat wires and connected a seperate zone valve to it for the heaters.

Comments

  • kpc_47
    kpc_47 Member Posts: 3
    why not...

    it should be fine....
  • Jed_2
    Jed_2 Member Posts: 781
    I think

    you want 2 L6006C-1018 Honeywell strap-on aquastats for that function, line voltage to start the fan when the SWT hits an acceptable temp. The ZVC can't do that.

    Jed