Gravity conversion boiler sizing
The Steam Whisperer (Formerly Boilerpro)
Member Posts: 834
so doors, windows, etc. need to be measured. Measuring the radiators will tell a contractor what temperature the system will operate at.....giving you a good idea of the potential effiency of a condensing type boiler. Condensing boilers are a match made in heaven for almost all hot water radiator systems.
No.3 appears to know what how to size boilers.
boilerpro
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=393&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
No.3 appears to know what how to size boilers.
boilerpro
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=393&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
There was an error rendering this rich post.
0
Comments
-
Gravity conversion boiler sizing
When sizing a replacement boielr for a gravity system, should you measure the radiators or the size of the rooms. I have had 3 contractors come out. Two of them measured the radiators and one of them measured all of the rooms, windows and door sizes and said the size of the radiators doesn't matter. I don't know who to believe.0 -
One out of three ain't bad
Measure the radiators for steam. Measure the heat loss of the building for hot water. Sounds like the last guy knows his stuff.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
I agree, go with Number Three
I would still ask him (or her?) to go over the heat loss numbers with you, what they mean and how that relates to the boiler selected.
I would also add that if the new boiler is a conventional non-condensing type, that the person install a bypass around the boiler to prevent too much boiler flow and to keep the boiler running above dewpoint. I suspect that person knows this but with true gravity systems being converted to pump operation for the first time, this sometimes is not done.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements