I have enough oil consumption to see the savings on the boiler at the Windsor Club in Newton, MA. This is a Smith Model 19 Series 6 that was fired with a 2.5 GPH nozzle, which matched the load. My feeling was that such a big boiler needed more firepower, so I installed a 3.5 GPH nozzle. Also, added a fan-in-can, since last year we had sooting from inadequate fresh air.
Last year, the system has absolutely NO main vents. I installed Gorton's on the mains. The steam pipes in the boiler room and some parts of the basement were uninsulated, so I insulated them.
Finally, and this is what makes the savings numbers hard to analyze: instead of heating the building to 70* from 8AM to 11PM daily , we keep it at 55* and only heat it on the three days a week that it is used. The place heats up remarkably well, without the expected cold feeling of the wall mass.
Oil savings on a degree day basis: 30%. Last year we used 5500 gallons.
My next project is to reinstall the LWCO/boiler feeder, since it is installed two inches too high, so the water level is always two inches above the normal line. Also, the boiler has a bullnose feeding the mains, so I want to re-pipe that in the off season. We're getting there. I'm finding it hard to find people who work with 3-inch and 4-inch pipe.
Last year, the system has absolutely NO main vents. I installed Gorton's on the mains. The steam pipes in the boiler room and some parts of the basement were uninsulated, so I insulated them.
Finally, and this is what makes the savings numbers hard to analyze: instead of heating the building to 70* from 8AM to 11PM daily , we keep it at 55* and only heat it on the three days a week that it is used. The place heats up remarkably well, without the expected cold feeling of the wall mass.
Oil savings on a degree day basis: 30%. Last year we used 5500 gallons.
My next project is to reinstall the LWCO/boiler feeder, since it is installed two inches too high, so the water level is always two inches above the normal line. Also, the boiler has a bullnose feeding the mains, so I want to re-pipe that in the off season. We're getting there. I'm finding it hard to find people who work with 3-inch and 4-inch pipe.
Steve from Denver, CO
0
Comments
-
Numbers are starting to come in
For the Ambassador Apartments, which we described in this thread:
http://forums.invision.net/Thread.cfm?CFApp=2&Thread_ID=59088&mc=13
the most recent gas bill showed a savings of 32.3%.
For Dmitri's Tavern, a rowhouse-type building with offices and rooms for rent on the second floor, the most recent bill showed a 20% saving on gas. This was the building where we had to thread a 2-1/2" steam pipe in place:
http://forums.invision.net/Thread.cfm?CFApp=2&&Message_ID=419297&_#Message419297
We also did a venting upgrade and replaced a plugged drip, which were responsible for a good part of the savings.
The most recent upgrade at the Bromo-Seltzer Tower- adding TRVs- saved them 10% on their steam consumption (they get their steam from the grid). Here's the thread:
http://forums.invision.net/Thread.cfm?CFApp=2&Thread_ID=57093&mc=14
More to come! If anyone has similar savings figures, feel free to post them here.
"Steamhead"
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements