Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
heatting saving 20%
Rich Swatton
Member Posts: 4
I have a house with 4 zones.
Main house #1
Family room #2
Office #3
Bathroom radiant #4
Heating boiler Munchkin 140M
Domestic Super Store 45 gallon
Boiler has outdoor re-set and domestic hot water priority
I wanted to minimize the boiler sequencing.
I took the largest demand zone main floor zone #1 and connected the thermostat and zone pump directly to the boiler.
The rest of the zones and pumps are connected to a Taco multi zone relay and disconnected the relay end switch.
The boiler only fires when the main zone calls. The other zones only call their pumps and not the boiler.
I lowered the domestic boiler temp set point to 155*f so the boiler will be in the condensing mode on a domestic call. Recovery is a little slower.
My savings this year compared to last year are over 20%.
Main house #1
Family room #2
Office #3
Bathroom radiant #4
Heating boiler Munchkin 140M
Domestic Super Store 45 gallon
Boiler has outdoor re-set and domestic hot water priority
I wanted to minimize the boiler sequencing.
I took the largest demand zone main floor zone #1 and connected the thermostat and zone pump directly to the boiler.
The rest of the zones and pumps are connected to a Taco multi zone relay and disconnected the relay end switch.
The boiler only fires when the main zone calls. The other zones only call their pumps and not the boiler.
I lowered the domestic boiler temp set point to 155*f so the boiler will be in the condensing mode on a domestic call. Recovery is a little slower.
My savings this year compared to last year are over 20%.
0
Comments
-
saving 20%
So, if I understand you correctly,, you turned the heat off in these zones & just circulated the system water?
Of course there will be savings,, I mean how can there not be?
Dave0 -
The heat was still on, the other zones they just didnt call the boiler.
They only got heat when the main house was calling..0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements