In Floor Heat
bruce_21
Member Posts: 241
Use foil faced insulation, at least R-19 but the more the better, and leave an inch or so gap between it and the subfloor.
0
Comments
-
In floor heat can't keep up when cold
I had a house built in Wisconsin with an outside wood boiler and a propane boiler backup. The hvac contractor stapled the wirsbo under the sublfoor between the floor trusses. The subfloor is 3/4" and then I have carpet, wood floor and tile on top of that. There are no heat plates and the cavity is not insulated. When it gets in the single degree range outside the thermostats can't keep up. The water leaving the wood boiler is 180 degrees but when it leaves the water to water heat exchanger it is 140 degrees. i know wood is not a good conductor of heat so my questions are:
1. Is there anything I can do to get the water temp. hotter after it leaves the heat exchanger?
2. Would installing heat plates and insulating the cavity help.(basement is unfinished so I have access) If so what do you reccomend.
any suggestions would be appreciated0 -
#2 is your ...
best bet. To go through 1 1/2" of wood then carpet is a lot to ask....I do not do staple up install w/o plates...kpc0 -
staple up
I concur. And may the floorce be with you. That was for you JMB0 -
I'm just a home owner who put his own radiant in. But, I think you would be well advised to put the plates in, AND use fiberglass insulation in those cavities. Install it so that it creates a pocket, it will direct the radiant energy towards the floor. I am in the middle of Michigan and my heating system is limited to 145, I have no carpet tho.
Good luck0 -
thanks for the input, I wil try the plates.0 -
PEX Underfloor
You definitely need to insulate below the pipe, and leave about a 2"-4" air gap. Plates will help, but not as much as insulating. I'd go with at least an R-19.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements