oil burner question
Big Ed_4
Member Posts: 2,992
What Type and size nozzle are you using ?
There was an error rendering this rich post.
0
Comments
-
I have a new install with Beckett Burner, V1 head in an MPO boiler. I cannot get the flame to stabilize after ignition. When ignition stops the flame gets smokey and noisey.
I have checked "Z" dimension and yes I zeroed first, electrode adjustment, run new oil line and filter (Garber), new nozzle, checked pump strainer, pump pressure @ 150 Spec, 12% co2, "0" draft, 0-smoke, stack temp about 380f. I tried with baffles in and out. Exterior chimney about 8" x 12".
Thanks for all help.0 -
Me too
We had the same problem a couple of weeks ago on an install and I also need to find out why. We put the ignition on with the motor for now but if it comes from the factory interrupted, I'd raher have it that way.
Ken F0 -
When you say the fire gets smokey, but you have a zero smoke,.. Im confused.
When you say noisey, could you describe it better? I'm having a hard time visualizing whats going on there.
Im just curious,
If jump out the FF terminals on the cad cell so that the burner is firing,.. what is the ohms resistance of the cad cell eye before and after ignition drops out?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"There was an error rendering this rich post.
0 -
Which MPO models
did you guys have? According to the Beckett OEM Spec guide, there are two V1 heads used on the larger MPOs- V1-0 with no static plate on the MPO-189 and the V1-3 with the 2-3/4-M plate on the MPO-231. Smaller ones use the L1 head.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Call us, 1-800-OILBURN, ask for tech service.0 -
Hago 45/W. If I let it run until the chimney gets hot it improves dramaticlly. Thats when I get the "0" smoke. On cold start it may shut down 2 - times.
The noise is a rumbling as if the flame is leaving the head.0 -
Hago 45/ss. If I let it run until the chimney gets hot it improves dramaticlly. Thats when I get the "0" smoke. On cold start it may shut down 2 - times.
The noise is a rumbling as if the flame is leaving the head.0 -
Ours was an 87
We haven't been back yet to reset it and troubleshoot as it was an emergency replacement job and got pushed into the schedule. I will check it and post back with any findings.
Ken F0 -
I Would Try....
.....a 60/solid or semi solid. Burnham has been recommending some odd nozzle sizes in the past. The were putting in Riellos .90 /80 with odd burner setting ,that ran rough and carboned up the end cone. I tend to first try the OEM and if it works great fine.
Wonder if the smoke is caused by a cold start ? There is a triple on the job right ....There was an error rendering this rich post.
0 -
Draft
What draft does the burner spec? They (Beckett) generally askes for -.02 draft. When the chimney gets hot your draft increases. Check your barametric damper see if you can get some draft on start up. Also is there enough make up air? We had a simular problem with a Carlin. After we asked the lady to leave the basement window cracked open a bit the problem went away. Just some thoughts. My $0.02 would be look at the draft. If you can call Beckett from the job site at 1-800-oilburn they will walk you through diffrent steps to find a solution. Each case presents a diffrent cause.
Mark0 -
Beckett
From past history, I'd change from a 45 degree nozzle. I'll ask my tech's. We have a number of New Yorker/Burnhams with the same problems.0 -
A 60 W delavan would work better0 -
Problem resolved. The boiler calls for '0' draft in the breach. Rechecked all settings abd all were good. Used same nozzle as spec and raised pump pressure to 25 psi to 175. Beautiful flame, 12.5 co2, 0 smoke, stack temp about 375. Starts quiet and runs smooth.0 -
Great!
now they'll be nice and warm for the holidays.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements