Growling 47-2
Every once in a while . It shakes the piping ,there is nothing else in the pipe that would cause it . Could it be high water pressure or just a bad seat.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=289&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
Welcome
It looks like you're new here. Sign in or register to get started.
  • Water pressure
    I always liked to see a PRV ahead of any feeder, electronic included. This allows control over feed rates, eliminates the singing and water hammer associated with float fillers.
    Simple boiler feeds with the factory 12# work well
  • Tom_80
    Tom_80 Member Posts: 22
    growler
    see if you can disconnect the piping on the leaving side of the feeder all the way to the pipe that enters the boiler. You tend to get a calcium build up right where the cold feed water enters the boiler and it creates a back pressure on the valve. Clean up the fittings and piping if scaled up. This some times leads to a boiler that over fills too.
  • RonWHC
    RonWHC Member Posts: 232
    The 47 & 51
    valve & strainer assembly has a plastic hexagonal poppet that closes against flow. It's a sloppy little bugger, & can shake the c/w feed line so it can be heard over much of a large building. Been there done that.
    H. D. is right. A pressure reducing valve ahead of the feeder takes care of the problem.
  • oil-2-4-6-gas
    oil-2-4-6-gas Member Posts: 641
    make sure the arrow is pointing towards the boiler --usually its the higher pressure on the inlet side prv will help --but i have run into a few where they were installed backwards -
  • bob young
    bob young Member Posts: 2,177
    try a shock arrestor
Welcome
