Help ID this steam system?

what you do need is proper piping.

I haven't looked at the I&O manual for that boiler but the lack of a header, Hartford Loop and possibly a second riser are certainly issues.

Generating 9 pounds of steam does a great job of compressing the steam, which takes up more water. This is likely the cause of the boiler shutting off on low water.

Gerry is right about those outboard traps. I couldn't see the brand name, but the one in the pic was made in Massachusetts.

How does the air get out of that system? There should be at least a vent on the dry return......