Boiler will not run

Have a 30-year old Weil Mclain CGi boiler (gas, hot water) that will not run when called by t-stat. It has water, 12#, the transformer is good, at the t-stat anyway, the pilot is burning, and I don't get it. It ran fine last season. No changes or alterations at all. Now she won't fire. Any ideas? Please my head is spinning.

Comments

  • Brad White_191
    Brad White_191 Member Posts: 252
    Thermocouple

    or gas valve would be the next things on my list. Pro-time at that point.
  • oil-2-4-6-gas
    oil-2-4-6-gas Member Posts: 641


    do you have batteries in the stat? --Energizer or Duracell only if you do --many of todays thermostats have batteries to make the switch
  • JB_8
    JB_8 Member Posts: 85
    spill switch

    Spill switch on? Check to see if you have a blocked flue pipe maybe a dead bird or other blockage?
  • Eileen Olive
    Eileen Olive Member Posts: 99
    Thanks

    The vent pipe is fine, no spill switch, and the wather heater is tied in to the same pipe. The stat has no batteries. I "thought," and I know the potential danger of that word, that the pilot would be out if the thermocupler went bad. If the circulator died, or seized, would the boiler still fire? I am grasping at straws at this point.
  • EJ you are correct if the pilot is lit

    the thermocouple is okay. Do you have 24 volts to the gas valve? If so and the valve does not open there is a good chance the valve is bad or it could be a broken ground back to the transformer.

    Yes the boiler will fire and the circulator could be bad and not run. If that is the case it would cycle on limit. Do you see a burner flame inside the boiler other than the pilot?
  • Timco
    Timco Member Posts: 3,040


    I'd check the controller by manually pushing the contacts together. if it fires right up, new controller time. That tells the boiler to fire and turns the pump on.

    Tim
    Just a guy running some pipes.
  • tim smith
    tim smith Member Posts: 2,807
    Could be bad flame roll out switch. Located right where burners

    go into combustion chamber on burner enclosure cover plate. Has 2 wires to it and has a ceramic holder and small fuse link. If this is open then you could have restriction in heat x or burners are corroded out. We find bad burners quite often on this vintage of boiler. Just a thought. Tim
  • oil-2-4-6-gas
    oil-2-4-6-gas Member Posts: 641


    there are many things that could be going on for DIY stick with the thermostat and call someone in for anything else -take the stat off of the sub-base jump r terminal to w terminal go downstairs see what happens if nothing then you need to call someone in