Boiler will not run
Eileen Olive
Member Posts: 99
Have a 30-year old Weil Mclain CGi boiler (gas, hot water) that will not run when called by t-stat. It has water, 12#, the transformer is good, at the t-stat anyway, the pilot is burning, and I don't get it. It ran fine last season. No changes or alterations at all. Now she won't fire. Any ideas? Please my head is spinning.
0
Comments
-
Thermocouple
or gas valve would be the next things on my list. Pro-time at that point.0 -
do you have batteries in the stat? --Energizer or Duracell only if you do --many of todays thermostats have batteries to make the switch0 -
spill switch
Spill switch on? Check to see if you have a blocked flue pipe maybe a dead bird or other blockage?0 -
Thanks
The vent pipe is fine, no spill switch, and the wather heater is tied in to the same pipe. The stat has no batteries. I "thought," and I know the potential danger of that word, that the pilot would be out if the thermocupler went bad. If the circulator died, or seized, would the boiler still fire? I am grasping at straws at this point.0 -
EJ you are correct if the pilot is lit
the thermocouple is okay. Do you have 24 volts to the gas valve? If so and the valve does not open there is a good chance the valve is bad or it could be a broken ground back to the transformer.
Yes the boiler will fire and the circulator could be bad and not run. If that is the case it would cycle on limit. Do you see a burner flame inside the boiler other than the pilot?0 -
I'd check the controller by manually pushing the contacts together. if it fires right up, new controller time. That tells the boiler to fire and turns the pump on.
TimJust a guy running some pipes.0 -
Could be bad flame roll out switch. Located right where burners
go into combustion chamber on burner enclosure cover plate. Has 2 wires to it and has a ceramic holder and small fuse link. If this is open then you could have restriction in heat x or burners are corroded out. We find bad burners quite often on this vintage of boiler. Just a thought. Tim0 -
there are many things that could be going on for DIY stick with the thermostat and call someone in for anything else -take the stat off of the sub-base jump r terminal to w terminal go downstairs see what happens if nothing then you need to call someone in0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements