zone valve on storage tank

Nick W_2
Nick W_2 Member Posts: 1
White Rodgers still makes the 1361-104 2-wire zone valve. Cv is 42.2.

Comments

  • shawn_14
    shawn_14 Member Posts: 14
    zone valves on storage tank

    What is the cons about using a zone valve on a storage tank? I am a storage tank to my system and have to existing zones already. The storage tank will be on proirity and the existing pump is large enough for the load. So what are the cons to it?
  • Bob Bona_4
    Bob Bona_4 Member Posts: 2,083
    every

    second counts on DHW recovery. Zone valves, especially Taco's heat style create lag while waiting for the end switch to make. Also, some ZV's Cv means flow restriction.

    Thirdly, 1 1/4 Zv's are hard to come by- some tanks need that size or bigger for correct flow.

    Fourthly, what pump curve may be good for heat loops, probably is not right for DHW flow rates.

    It's done anyway, and some end users get away w/ it b/c of lower DHW demands/variables, but it's not something I would do. I advocate a dedicated, properly sized pump for the DHW.
  • Brad White_191
    Brad White_191 Member Posts: 252
    Well if what Bob wrote

    does not convince you, what can anyone else say? Convinced me! Bob, how do you really feel about this? :)
  • Bob Bona_4
    Bob Bona_4 Member Posts: 2,083
    :) nm

  • steveex
    steveex Member Posts: 95


    I have twined honeywell 1" zone valves for 119 superstor tank, the larger gpm zone valve that is. Parallel of course.
  • hot_rod
    hot_rod Member Posts: 23,371
    Depends on the load

    and how many GPM's you are moving.

    Most ZV, at least Caleffi :) have a 7.5 Cv up to 1-1/4". They easily allow 75,000 at a 20 delta t.

    I've used 1" 3 way zone valves on a bunch of Knight 80,000 boilers, they work great. Use a 120V operator and power the zone valve right from the mod-con DHW priority position. Simple one pump operation, easy to pipe also.

    White Roger had that full port 1316 ZV for years. You could drive a (small) truck through that valve.

    hr
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream