2 Pipe Vacuum Return

Big Ed_4
Big Ed_4 Member Posts: 3,019
Can you post a system diagram ? I know it will help us help you ...

There was an error rendering this rich post.

Comments

  • matt_63
    matt_63 Member Posts: 10
    2 Pipe Vacuum Return

    If an accumulator tank (with no pumps) is used in a vacuum return system should the tank be under a vacuum. The vacuum tank/pumps is pulling condensate return up from the accumulator tank. The vacuum gauge on the vacuum tank reads 10"hg. The air vent on the accumulator tanks is blowing air out. The vacuum pumps run constantly and when they are shut off the vacuum drops to 0 within seconds. Is my accumulator tank piped incorrectly?
  • If you are referring

    to the hurling water tank; the vacuum pump uses water in the tank for lubrication & vents the air, pulled from the system, out the vent on the hurling water tank.

    Most systems, we work with, operate in the 3 to 8" vacuum range. Sounds like a big pump on a system w/ many leaks.
  • matt_63
    matt_63 Member Posts: 10
    2 pipe vacuum return

    Attached is a photo
  • Check page 192

    of "The Lost Art of Steam Heating". Your setup is shown and described there.