Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Near boiler piping heights

Dave M
Dave M Member Posts: 36
Am doing near boiler piping with 5 circs pumping away. Regarding the elevations of the black iron piping for this, is it perfectly acceptable to have the air scoop and expansion tank up near celing height and out of the way and then run the black iron back down to waist height where the mainfold will be for the circulators? Certainly easier to maintain circulators that way. I'm assuming this doesn't create any air issues going up from the boiler supply and then back down to circulators before going copper out to the zones?

Comments

  • bob young
    bob young Member Posts: 2,177
    airbound

    lines could possibly get air locked. heel tees with bleeders might be good insurance.
This discussion has been closed.