York defrost boards
ddlong1286@yahoo.com
Member Posts: 139
Hi all,
Need info on a York defrost board. It flashes 5 times. It is a 031-00832 and made by honeywell. The literature is faded and can't read.
Anyone have the lit for it? There are multible units at this school.
Thanks
Don In Moberly MO
Need info on a York defrost board. It flashes 5 times. It is a 031-00832 and made by honeywell. The literature is faded and can't read.
Anyone have the lit for it? There are multible units at this school.
Thanks
Don In Moberly MO
0
Comments
-
#5 fault
Is a defrost fault. The control has to calculate a "default defrost" on Two consecutive defrost cycles. This is usualy caused by a faulty liquid line sensor, or low refrigerant charge. The sensor is a standard 10K sensor and should read 32,000ohm @32'F ( ice water). That unit with a clear coil should have a liquid line temp. that is 10' below ambiant when the refrigerant charge is correct. Hope this helps!
Steve0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements