1000' pex
tim smith
Member Posts: 2,807
pumping the bejeebees out of it and got the heat to fairly stable. The idea of reversing is interesting, don't know which is better but this worked to get a customer out of jam. Told customer no promises before hand although. Tim
0
Comments
-
1000' pex
well it happened again. I went over to a new builder/client this evening. Three years ago he had licensed plumber/friend run radiant tubing into a new slab area in his own house. He purchased and ran a 1000' roll of 1/2" pex from the boiler and back into a 10' by 44' area on slab. He is running a 0012 taco pump and of course it takes forever to heat up and the end of the loop never heats. Oh, and the thermostat is in the wrong place too. He showed me pictures of what was run. Nice and neat and about 8-9" on center over an insulated slab.
I guess I have choices....#1 is run as fast as I can. Any brainstorms guys?? I have some additional solutions but I don't know if it is worth it.
Has anyone come across this with any success?
Thanks,
Brian0 -
Calculate the total head and select 2 circs doubled up with 2 low flow high head circs, 1 one supply 1 at return wired together.
Add supplemental heat from there if necessary0 -
Hot Rod had a somewhat solution to this. Some sort of 4-way valve if I recall that reversed the flow periodically.
Either that or get out a jackhammer.0 -
reverse
flow every 5 minThere was an error rendering this rich post.
0 -
Alotta pex
Ran into simalar situation several years back. contractor put 900 feet + in driveway told client to hook up a 40 gal. water heater and he could have snowmelt. wouldn't work then an I dought if it will work now.0 -
Paxton has the parts
to assemble the reverser I used. Here is the link to the how and whys.
www.pmmag.com/Articles/Column/625c61cba20d7010VgnVCM100000f932a8c0____
I'd still pump it up, maybe a 26-99 or so, even with the reverser.
hrtBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Dito to Stephen and Bob(4 way); Jack von hammer; Or run.0 -
8" on center 120" wide at 44' is approx 660 Ln/ft not 1000' mentioned. if the area is 440 sq/ft approx 25 btu per ft = 11,000 btuh load, or 1.1 gpm at 20 degree delta T. .04079 friction loss per ft X 660'= 27 ft hd. Design is 1.1 gpm @ 27 ft. The taco 009 would work. Anyone have any comments on my way of thinking???Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0 -
'1000 radiant
The right way would have 2 circuits right or is '600 comon practice.Just wondering how you would have done it.0 -
Pump it up, low temp, const. circulation0 -
Taco i-series to the rescue0 -
1000 ft loops
I had a guy put 2 1000 ft loops, a 150 and a 35 on a four loop manifold. Used a 009 and choked the bejeebers out of the short loops; and surprisingly, it heats the slab. Pretty much constant circ with OD reset.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements