1000' pex

tim smith
tim smith Member Posts: 2,807
pumping the bejeebees out of it and got the heat to fairly stable. The idea of reversing is interesting, don't know which is better but this worked to get a customer out of jam. Told customer no promises before hand although. Tim

Comments

  • Brian_11
    Brian_11 Member Posts: 18
    1000' pex

    well it happened again. I went over to a new builder/client this evening. Three years ago he had licensed plumber/friend run radiant tubing into a new slab area in his own house. He purchased and ran a 1000' roll of 1/2" pex from the boiler and back into a 10' by 44' area on slab. He is running a 0012 taco pump and of course it takes forever to heat up and the end of the loop never heats. Oh, and the thermostat is in the wrong place too. He showed me pictures of what was run. Nice and neat and about 8-9" on center over an insulated slab.

    I guess I have choices....#1 is run as fast as I can. Any brainstorms guys?? I have some additional solutions but I don't know if it is worth it.

    Has anyone come across this with any success?

    Thanks,

    Brian


  • Calculate the total head and select 2 circs doubled up with 2 low flow high head circs, 1 one supply 1 at return wired together.

    Add supplemental heat from there if necessary
  • Stephen C.
    Stephen C. Member Posts: 60


    Hot Rod had a somewhat solution to this. Some sort of 4-way valve if I recall that reversed the flow periodically.

    Either that or get out a jackhammer.
  • bob_46
    bob_46 Member Posts: 813
    reverse

    flow every 5 min

    There was an error rendering this rich post.

  • PLUMBARIS
    PLUMBARIS Member Posts: 22
    Alotta pex

    Ran into simalar situation several years back. contractor put 900 feet + in driveway told client to hook up a 40 gal. water heater and he could have snowmelt. wouldn't work then an I dought if it will work now.
  • hot_rod
    hot_rod Member Posts: 23,166
    Paxton has the parts

    to assemble the reverser I used. Here is the link to the how and whys.

    www.pmmag.com/Articles/Column/625c61cba20d7010VgnVCM100000f932a8c0____

    I'd still pump it up, maybe a 26-99 or so, even with the reverser.

    hrt
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Derheatmeister
    Derheatmeister Member Posts: 1,579


    Dito to Stephen and Bob(4 way); Jack von hammer; Or run.
  • Joe Mattiello
    Joe Mattiello Member Posts: 718


    8" on center 120" wide at 44' is approx 660 Ln/ft not 1000' mentioned. if the area is 440 sq/ft approx 25 btu per ft = 11,000 btuh load, or 1.1 gpm at 20 degree delta T. .04079 friction loss per ft X 660'= 27 ft hd. Design is 1.1 gpm @ 27 ft. The taco 009 would work. Anyone have any comments on my way of thinking???
    Joe Mattiello
    N. E. Regional Manger, Commercial Products
    Taco Comfort Solutions
  • MARK_123
    MARK_123 Member Posts: 4
    '1000 radiant

    The right way would have 2 circuits right or is '600 comon practice.Just wondering how you would have done it.
  • steveex
    steveex Member Posts: 95


    Pump it up, low temp, const. circulation
  • steveex
    steveex Member Posts: 95


    Taco i-series to the rescue
  • Plumdog_2
    Plumdog_2 Member Posts: 873
    1000 ft loops

    I had a guy put 2 1000 ft loops, a 150 and a 35 on a four loop manifold. Used a 009 and choked the bejeebers out of the short loops; and surprisingly, it heats the slab. Pretty much constant circ with OD reset.