What's wrong with this picture?
Steamhead (in transit)
Member Posts: 6,688
looks like they slid the old boiler to the side and hooked the new one up the same way.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
What's wrong with this picture?
Went on a no heat call this afternoon. Water is running out the bottom of the five year old W-McL SGO-3 about as fast as it will go in. Seems the unit cracked. There are burn marks in the middle of the jacket which point to fire escaping between the sections. But check the piping.0 -
The electrical panel deserves special mention, too.
Has there been any professional level work done there?0 -
What's right with this picture?
Zero.0 -
Hmmmm
I wonder how it even heated? Lots of wet steam. I hope the owner is appreciative of a professional install.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements