Circulator cutting off on hydronic boiler
Duane
Member Posts: 17
This weekend I attempted to help my brother with some problems he is encountering after replacing his circulator. The system is a 1930's radiator and pipoing with a 50's boiler. For the 1400sf house the radiators appear quite large to me as do the 2" headers for each loop. There are 2 headers, one for supply and one for return, on each loop, sloped up toward the convectors.
Problem 1 is the radiators will not bleed fully. The first floor sees the bottom 2/3 of the radiators hot, and the second floor they are cold. The pressure gage shows 0 when circulator is not running, and 10 psi when it is running. Opening the manual radiator bleeders gives air for a short period of time, then the air stops, whether the circulator is running or not. Hours of trying will not make the water line rise.
I believe the make-up water pressure regulator is clogged and thus is not letting in more than a slow trickle of water, if any, so the system pressure drops to zip when you try to bleed. Does this make sense? This being the case, anyone got info on how to clean out the Bell & Gossett red regulator units circa about 1955?
Problem 2 is the circulator control. When the hi limit is reached on the aquastat, the circulator turns on as one would expect and the water begins to flow. However, due to the large headers and radiators being full of cold water, the boiler temperature plummets quickly and the circulator shuts back off. I noticed the aquastat has both high and low settings, which were set at 180 / 140. The temp went below 140 in a minute or so and the circulator shut off. I know this is to preserve heat for the hot water coil, but this seems very wasteful in that the circulator starts and stops several times before serving the whole loop. What are the proper settings, considering that the large electric hot water heater uses the coil for a boost, and not for the entire job of heating domestic hot water?
Thanks and God bless.
Duane
Problem 1 is the radiators will not bleed fully. The first floor sees the bottom 2/3 of the radiators hot, and the second floor they are cold. The pressure gage shows 0 when circulator is not running, and 10 psi when it is running. Opening the manual radiator bleeders gives air for a short period of time, then the air stops, whether the circulator is running or not. Hours of trying will not make the water line rise.
I believe the make-up water pressure regulator is clogged and thus is not letting in more than a slow trickle of water, if any, so the system pressure drops to zip when you try to bleed. Does this make sense? This being the case, anyone got info on how to clean out the Bell & Gossett red regulator units circa about 1955?
Problem 2 is the circulator control. When the hi limit is reached on the aquastat, the circulator turns on as one would expect and the water begins to flow. However, due to the large headers and radiators being full of cold water, the boiler temperature plummets quickly and the circulator shuts back off. I noticed the aquastat has both high and low settings, which were set at 180 / 140. The temp went below 140 in a minute or so and the circulator shut off. I know this is to preserve heat for the hot water coil, but this seems very wasteful in that the circulator starts and stops several times before serving the whole loop. What are the proper settings, considering that the large electric hot water heater uses the coil for a boost, and not for the entire job of heating domestic hot water?
Thanks and God bless.
Duane
0
Comments
-
replace the feed
Personally, I never had any luck cleaning out a reducing valve that old. Too much time involved draining and refilling that huge system to mess around w/ 50 year old parts. We use Watts 911s comb. backflow/ reducing valves as replacement. While ur at it, add a ball valve before and after it and make the job easier next time. no draining. The settings are generally at 180/ 160 20'dif.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements