Drips for steam mains..BP

flows downhill as you say, what would remove the condensate from it?

Unless it was properly sized for counterflow, I would definitely put in a drip trap assembly. 1/2" or 3/4" F&T at least, if low pressure. An Inverted Bucket type if higher than 15 PSI.

Comments

  • how far

    I have a system with a newer 3 inch steam main 75 feet long that runs downhill from the boiler header . It has no takeoffs and then just feeds a 2 inch one pipe steam main that will drip back to the boiler water line. Does this 75 foot line need a drip. I can repipe the connetion from the 3 to the 2 so the condensate can just flow from the 3 inch main into the 2 inch main. All the mains will be insulated, so we are mainly just dealing with startup condensate. The 2 inch line feeds about 350 EDR.

    Boilerpro

    There was an error rendering this rich post.

  • Clarification......

    the 3 inch line runs downhill away from the boiler and then can flow into the 2 inch line that flows downhill back to the boiler return.

    BP

    There was an error rendering this rich post.

  • It would probably work OK

    but if there is a way to drip that 75-footer, I would. If anything happens to increase the amount of condensate in it, it might bang at the transition if not dripped.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"