Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Venting
Boston_2
Member Posts: 107
I think I found the cause of my missing water problems, I discovered my new Gordon #2 main vent was not operating correctly and it appears that it was leaking steam through the entire cycle. Amazing, it looks like I was loosing about a cup of water each cycle.
With the new Main vent in place, the system is working great other then several of my radiator vents are now making venting/gurgling noises once that radiator is fully hot. I have all new radiator vents, Varivalve and MaidOmist vents.
Thoughts?
With the new Main vent in place, the system is working great other then several of my radiator vents are now making venting/gurgling noises once that radiator is fully hot. I have all new radiator vents, Varivalve and MaidOmist vents.
Thoughts?
0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements