Venting
Boston_2
Member Posts: 107
I think I found the cause of my missing water problems, I discovered my new Gordon #2 main vent was not operating correctly and it appears that it was leaking steam through the entire cycle. Amazing, it looks like I was loosing about a cup of water each cycle.
With the new Main vent in place, the system is working great other then several of my radiator vents are now making venting/gurgling noises once that radiator is fully hot. I have all new radiator vents, Varivalve and MaidOmist vents.
Thoughts?
With the new Main vent in place, the system is working great other then several of my radiator vents are now making venting/gurgling noises once that radiator is fully hot. I have all new radiator vents, Varivalve and MaidOmist vents.
Thoughts?