Air flow in PVC.....

bigugh_4
bigugh_4 Member Posts: 406
You could use steel pipe's informatiom for this. at least the air should move slightly easier through the PVC.

Comments

  • DrPepper
    DrPepper Member Posts: 29
    Air pressure drop in PVC pipe...

    Here is an odd ball question. I have a research facility project that has 32 bathtub sized isolation enclosures. I'm to pull filtered outside air thru a hydronic coil, thru the enclosures (negative pressure to room) to maintain about 70F, and out thru another set of HEPA filters with a Spencer turbine vacuum pump. All the ductwork is PVC. I've looked in ASHRAE, google(radon sizing,etc.) and haven't found a chart for AIR pressure drop in PVC. 2" thru 4" sched 40, from 0 to 350 cfm. None of the round metal duct charts go down below 4". I want to get some idea what my pressure drop is for the system circuits at max air flows. Any ideas???

  • mark_120
    mark_120 Member Posts: 6


    condensing furnace and boiler manf. use pvc as air transport to there units I would select a unit that the BTUs can be translated to a combustion air to gas ratio 1:1 or .9:1 and use there fitting chart. for your application a 350M boiler combustion air design should supply you with the answer.