Is my boiler oversized ?
Options
HQ
Member Posts: 4
This is my first posting.
I'd like first to thank everyone on the Wall for teaching
me everything I know about steam heating. Reading the Wall
is so addictive.
My boiler is working fine; but I need your help to determine if my calculation is correct that the boiler is oversize.
Radiator made: American Standard,
5 tube type, 2.5" section-section
Room Height Sections Sq. Ft. Steam Sq. Ft. Steam
(inch) (per sec) (per radiator)
------------------------------------------
Foyer 38 14 5 70
DNing 38 9 5 45
Brm1 38 8 5 40
Brm2 38 8 5 40
Brm3 38 6 5 30
Brm4 38 6 5 30
Attic 38 4 5 20
LRm 20 20 2.67 53.3
Kit 20 13 2.67 34.7
Bth 18 8 2.25 18
-----------------------------------------
Total 381.0
System Info:
Installation date:
Single pipe steam:
Parallel flow system with Wet return + Hartford loop
Insulation: All the mains + returns
2 end of main vents: Gordon #2
Boiler Info: Weil-Mclain EG-50
Boiler Rating:
Input: 175000 Btuh
Output: 145000 Btuh
Sq. Ft. Steam: 454 (I hope this include 33% pickup factor)
Calculation:
(381/454)*100 = 83.92%
I'd like first to thank everyone on the Wall for teaching
me everything I know about steam heating. Reading the Wall
is so addictive.
My boiler is working fine; but I need your help to determine if my calculation is correct that the boiler is oversize.
Radiator made: American Standard,
5 tube type, 2.5" section-section
Room Height Sections Sq. Ft. Steam Sq. Ft. Steam
(inch) (per sec) (per radiator)
------------------------------------------
Foyer 38 14 5 70
DNing 38 9 5 45
Brm1 38 8 5 40
Brm2 38 8 5 40
Brm3 38 6 5 30
Brm4 38 6 5 30
Attic 38 4 5 20
LRm 20 20 2.67 53.3
Kit 20 13 2.67 34.7
Bth 18 8 2.25 18
-----------------------------------------
Total 381.0
System Info:
Installation date:
Single pipe steam:
Parallel flow system with Wet return + Hartford loop
Insulation: All the mains + returns
2 end of main vents: Gordon #2
Boiler Info: Weil-Mclain EG-50
Boiler Rating:
Input: 175000 Btuh
Output: 145000 Btuh
Sq. Ft. Steam: 454 (I hope this include 33% pickup factor)
Calculation:
(381/454)*100 = 83.92%
0
Comments
-
Is my boiler oversise ?
I'm a homeowner and This is my first posting.
I'd like first to thank everyone on the Wall for teaching
me everything I know about steam heating. Reading the Wall
is so addictive.
My boiler is working fine; but I need your help to determine if my calculation is correct that the boiler is oversize.
Foyer 38 14 5 70
DNing 38 9 5 45
Radiator made: American Standard, 5 tube type, 2.5" section-section
Height Sections Sq. Ft. Steam/section Sq. Ft. Steam/radiator
-----------------------------------------
Total 381.0
System Info:
Installation date:
Single pipe steam:
Parallel flow system with Wet return + Hartford loop
Insulation: All the mains + returns
2 end of main vents: Gordon #2
Boiler Info: Weil-Mclain EG-50
Boiler Rating:
Input: 175000 Btuh
Output: 145000 Btuh
Sq. Ft. Steam: 454 (I hope this include 33% pickup factor)
Calculation:
(381/454)*100 = 83.92%0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements