pump
paul_91
Member Posts: 62
ive been told that a taco 007 circ pump can only pump up to 1 1/4 inch pipe ....is that true ? im replacing a boiler and the mains are 2 inch.
0
Comments
-
A 007 will almost always work on a converted gravity system. It is head that counts, which includes pipe size, convector type, and total feet of supply & return on the zone to be pumped. You may only be able to find 1.25" flanges, but just reduce at the iron pipe ends.
TimJust a guy running some pipes.0