Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
pump
paul_91
Member Posts: 62
ive been told that a taco 007 circ pump can only pump up to 1 1/4 inch pipe ....is that true ? im replacing a boiler and the mains are 2 inch.
0
Comments
-
A 007 will almost always work on a converted gravity system. It is head that counts, which includes pipe size, convector type, and total feet of supply & return on the zone to be pumped. You may only be able to find 1.25" flanges, but just reduce at the iron pipe ends.
TimJust a guy running some pipes.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements