burnham scg gas boiler control problem
paul_92
Member Posts: 8
check if you have 24 v at the y terminal on that control when you have the t-stat disconnected .. you shouldnt have voltage there when theres no call for heat
0
Comments
-
control problem with burnham scg gas boiler
I started a burnham scg gas boiler today and it runs continuously without any call for heat, tt disconnected and it only shuts down by the hi limit control.
I replaced the combo transformer/relay, honeywell R8285D, still the same problem. The blower relay pulls in as soon as the boiler is energized and the boiler fires up. It seems that there may be a problem with the factory control wiring. Any suggestions.
CG
0 -
t stat
so you replaced the fan center..make sure with your meter that the t-stat isnt calling between terminals r and g ... the problem has to be at that point ..unless there are some serious wiring issues and you need to get a pro0 -
The t-stat wires are disconnected from the relay and it still cycles.0 -
????
when you replaced that control did you replace the relay that was in it too??0 -
I put the original control back in and I have the same problem. The customer has heat for the weekend and I'll be back there Monday to check the voltage at the y terminal. thanks for the input.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements