triangle tube solo110
michael_33
Member Posts: 4
we just installed our first mod con boiler which are the triangle tube prestige solo 110 they seem to be well built and worked perfect at start up,, my only concern is when using the out door reset and max temp left at 186 factory setting.. when its 62 outside boiler water is held to around 88 degrees, sure seems low and different for baseboard from past thinking... is there other settings that i am missing or is the design temp for 0 degee day all that is needed to be set with out door reset,,, thanks mdh
0
Comments
-
You can change your minimum temp from 86 to say a 100 if you
find that the 84 degrees at 60 or so does not do the job. There is also a shift setting that I don't normally find a need for. You can change your warm weather shut down up or down to change the ramp of your reset. Several ways to modify water temp to od temp. Good luck, Tim0