LP boiler
michael_4
Member Posts: 31
Hello all,
I was checking a LP fired boiler the other day and the best Supply temp. I could get after 15 min. runtime was 100 deg. F.
The LP pressure inlet to gas valve was 11" w.c. and the tank outside showed 40% full. Valve was marked with conversion sticker. The outlet tap was sheared so no removing it and checking outlet pressure.
It was a Weil-Mclein.
Pump was B&G blue colored at 1/20 h/p. Sorry no model numbers.
I removed and cleaned burners, pilot assembly and heat exchanger flue passages with brush.
Any ideas?
Thanks in advance,
Michael
I was checking a LP fired boiler the other day and the best Supply temp. I could get after 15 min. runtime was 100 deg. F.
The LP pressure inlet to gas valve was 11" w.c. and the tank outside showed 40% full. Valve was marked with conversion sticker. The outlet tap was sheared so no removing it and checking outlet pressure.
It was a Weil-Mclein.
Pump was B&G blue colored at 1/20 h/p. Sorry no model numbers.
I removed and cleaned burners, pilot assembly and heat exchanger flue passages with brush.
Any ideas?
Thanks in advance,
Michael
0
Comments
-
You may have 11" WC pressure but you are lacking volume. There is probably something blocking your gas line partially.Good Luck!0 -
Sounds like you
may have the wrong size orifices. Perhaps who ever converted it did not size correctly. How many burners do you have and what is the required input? Give me that and I will size them for you. Do you have an orifice drill kit?
If this is not familar to you then get the LP company to come in and check things.0 -
too much load?
what's the boiler connected to? Any high mass system, radiant, cast radiators, etc can keep the boiler running cold at start up.
If there is a valve downstream from the circ pump try throttling it down and see if the temperature rises.
hrBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Gotta know the outlet pressure
Like Tim says; verify that the orifice size is correct. You might be able to remove one burner, and slip rubber tubing over one orifice and get your pressure reading that way. The gas valve would have to have been converted to LP pressure, if it wasn't you will be way underfired. Be careful.0 -
Hello all,
Tim, there are 8 burners.
Hot Rod, 2 zones of approx. 50'each of 3/4" fin-tubed baseboard. Very small home(1700 sq. ft.).
I will advise client that we have several options. First will be read outlet gas valve pressure and see if orifices have number sizes stamped on them. If no marking will order new ones based upon load calc. and required fuel output. Then if that does not help we will look at clogged fuel line.
Thanks for your time guys,
Michael0 -
Mike, a few questions
Mike,
Is this a new install or an existing system?
If it is new, then you have to large of a load, or the input is not adequate.
If existing, how old is it?
If it is an existing, did it ever maintain higher temps.
If it is existing and did maintain higher temps, what has changed?
Just a few things to think about
Ed Carey0 -
What is the input
give me that and the outlet pressure and with the eight burners I can tell you what size orifices you need.0 -
Mr. Carey,
This install is from mid 1980's. The couple that lives there have been satisfied with the boiler since they never turn the tstats above 64 deg. F. They told me if it becomes an issue of not heating this winter they would like me to follow-up. I would like to get a head start either way.
Tim,
When I call them this week to let them know what I have learned, they may ask me to return and get that info. and I will pass it on to you.
Thanks everyone for there input,
Michael0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements