oil burner
Options
paul_91
Member Posts: 62
im having a problem with a riello burner....i have 120 volts at the primary control, the motor runs , the transformer sparks, i have good oil flow, but no oil comes out of the jet line ... so i replaced the delayed oil valve that sits in top of the fuel pump...still nothin happens....i also switched the primary control and i still have no oil comin out of the jet line .... the oil valve has 3 wires going to it..am i missing something?? any suggestions
0
Comments
-
no oil flow
Fire-o-matic valve is closed or the handle is bad. Stem shoud be sticking up. Solder in handle broke and valve shut.
Pump strainer in side pump is plugged.
The pump coulping is slipping.
The metal yoke that goes around the oil valve is missing.
Wires for valve is connected to wrong terminals.
The pump is no good.There was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 168 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements