oil burner

paul_91
paul_91 Member Posts: 62
im having a problem with a riello burner....i have 120 volts at the primary control, the motor runs , the transformer sparks, i have good oil flow, but no oil comes out of the jet line ... so i replaced the delayed oil valve that sits in top of the fuel pump...still nothin happens....i also switched the primary control and i still have no oil comin out of the jet line .... the oil valve has 3 wires going to it..am i missing something?? any suggestions

Comments

  • Big Ed_4
    Big Ed_4 Member Posts: 2,992
    no oil flow

    Fire-o-matic valve is closed or the handle is bad. Stem shoud be sticking up. Solder in handle broke and valve shut.

    Pump strainer in side pump is plugged.

    The pump coulping is slipping.

    The metal yoke that goes around the oil valve is missing.

    Wires for valve is connected to wrong terminals.

    The pump is no good.