New Burnham IN6 gas boiler -Is something clogged?
Ted Robinson
Member Posts: 126
We have just started running the heat on a National Grid deal, Burnham IN6. My added run time meter is presently on 13.5 hours, just a 'baby'.
Once fired up, the standard gauge moves up to a rather high reading of 8 psi,while the extra gauge sees no increase in pressure. The pressuretrol set at < 1psi and I doubt it has reached cutoff yet. The probe low water cutoff does cycle every 20 minutes.
The standard pressure gauge, 0 - 30 psi is installed on the left side, tapping B. The pressuretrol and a 0 - 15 psi gauge are connected to tapping H. The boiler was piped with two, 2 in risers and a 2 in drop header.
So, is this high internal pressure normal, or does it indicate an internal problem?
The Pro is due back soon for a boiler water skimming procedure.
Once fired up, the standard gauge moves up to a rather high reading of 8 psi,while the extra gauge sees no increase in pressure. The pressuretrol set at < 1psi and I doubt it has reached cutoff yet. The probe low water cutoff does cycle every 20 minutes.
The standard pressure gauge, 0 - 30 psi is installed on the left side, tapping B. The pressuretrol and a 0 - 15 psi gauge are connected to tapping H. The boiler was piped with two, 2 in risers and a 2 in drop header.
So, is this high internal pressure normal, or does it indicate an internal problem?
The Pro is due back soon for a boiler water skimming procedure.
0
Comments
-
Sounds like
the standard gauge is shot . Was it connected directly to the boiler ? Or was it after a pigtail ? Here's an install we did yesterday showing where we pipe the gauge . They seem to last alot longer with the protection of the pigtail . But truth be told , alot of them are junk right out of the box . And if you hand tighten the gauge all the way you can screw up the dial too .0 -
Thanks for the alternate suggestion.
The supplied "internal siphon" gauge was threaded directly into the boiler tapping. It does rest at "0", and then go up many psi during steaming. My second gauge is installed similar to your method.
And if the boiler was actually at 8 psi, my testing of the pressure relief valve would be far more dramatic than it is now.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements