Dry Return piping
Stewy_2
Member Posts: 83
both have 1" dry returns. Can I meet the dry returns to the same vertical drip connection if I can keep the minimum "A" dimension? If so how should it be piped, Im assuming no bull head tee. Also a question about the equalizer pipe. I wanna use 2". How far down should I go? Can I reduce it at the tee for the close nipple to the Hartford loop? Thanks
0
Comments
-
First answer- No
Each dry return must have its own drip below the waterline. This keeps air and steam from passing from one dry return to the other. This can cause banging.
For the equalizer- what is the minimum size specified for your boiler?
"Steamhead"
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
It is 1 1/2\" but I'd like to take Mr. Holohans suggestion
from the Lost Art of Steam and atleast go 2". Is that the right thing to do?0 -
That must be why
Dan wrote that, I would assume0 -
Hmmmmm.... Good point:{)0 -
I didnt exactly mean it like that
0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements