    Tim_64 Member Posts: 76
    Another steam vent question.

    Can you guys take yet another steam vent question?

    This is probably a combined vent/control question.

    I've install a new boiler (a bit over sized to allow for a future addition) and all new main and radiator vents per the "Balancing" e-booklet.

    I'm still getting a bit of hissing and spitting from the vents, the old slow vents were silent. Could the hissing be from higher pressure? In the balancing book all values are based on 1-3 oz of pressure. The lowest pressure I can run my system on (now) is pressuretrol set at 0.5# with 1# dif. I attached a gauge to the radiator farthest from the boiler (see attached) and it registers about 1.5# just as the pressuretrol cuts the burner.

    Are the vents acting as expected? today it took 35 minutes to raise the interior temp 6 deg (outside is 48) and the system bumped the pressuretrol 4-5 time during that burn.

    My strategy is to install a vaportrol, underfire the burner, and revisit the vents I've installed..

    So is my system behaving as expected?

    thanks for your patience
  • David Nadle
    David Nadle Member Posts: 624


    Tim, I'm a homeowner, but I have some experience with a new boiler. I think you have wet steam. Assuming your near boiler piping is OK (you should post pics), you might have to skim the boiler a few more times. My new boiler was skimmed three times and cold skimmed twice before it started to behave.

    In my opinion a vaportrol is not going to help you diagnose the problem, but will be a good addition once everything works satisfactory.

    If your mains are not insulated that's a must. Insulating the takeoffs also made a huge difference in my case. This solved my panting radiators problem.

    Another tip, while you're trying to figure everything out I recommend you use cheapo rad vents. Between the dirty boiler and the panting I destroyed a whole bunch of vents over the first season. It took almost the whole first season of trial and error to get things right.


  • Tim_65
    Tim_65 Member Posts: 8


    I know the vaportrol isnt a cure, but will offer more granular control of the system since its scale is 0-4 psi rather that 0.5-9 psi.

    All the mains are insulated, and I've been skimming the boiler every day. There is very little oil left in the skim water, though the water is colored like strong tea now, rather than weak tea. I suppose I'll keep skimming till it cleans up. BTW the water in the sight glass only varies max 1 in when steaming, usually between 1/2-3/4 in

    The one issue may be the riser piping. I installed this boiler before I found this resource. I'll take a picture when I get home (I work nights).
  • gerry gill
    gerry gill Member Posts: 3,078
    post your boiler pictures

    so we can see the piping..also two stage firing is always my recommendation..a vaporstat alone will only make it cycle more often and sooner.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • Tim_65
    Tim_65 Member Posts: 8


    Ive been wondering whether anyone varies the firing rates of oil burners for steam, seems like with pwm circuitry you could adjust the amount of flame etc.

    I'll get some pictures tomorrow
  • Tim_64
    Tim_64 Member Posts: 76
    pics

    Here is a picture of the piping.

    Today I monitored the system during one of it cycles. I set the thermostat to increase room temp 5 deg (62 to 67)

    Since two of the three mains are in crawlspaces and difficult to access I checked for steam at the farthest radiator valves.

    It took about 7 minutes for the valves to get hot to the touch (each of those mains is vented with a Gorton 1 & 2)
    It took 30 minutes to raise the temp 5 deg (48 deg outdoors)

    the sight glass seems to be pretty stable now around 1/2 in or less of bouncing

    The vents still hiss a bit though

  • V8toilet
    V8toilet Member Posts: 71


    You mentioned that you over sized the boiler to accommodate a future upgrade. A steam boiler that is too large for the radiation in your home will short cycle and cause some vents to hiss if the pressure gets high. How over sized is your boiler?

    You may need to get an expert in there to maybe down fire your boiler to try and match the boiler input to the connected load in your home.

    I know that if I shut down a couple of my larger radiators and thus reduce my connected load on my boiler that the pressure in the system goes up and my vents start to hiss because the boiler is putting more steam into the system that it can condense.

    Also it looks from that picture like the near boiler piping isn't really the ideal way to pipe it for steam.
  • David Nadle
    David Nadle Member Posts: 624
    Skimming

    When there's oil floating on the surface of the water it makes for a surging boil and wet steam. Skimming involves removing a cap or plug in a tapping or pipe just above the waterline, then firing the boiler until a great gush of boiling hot water shoots out into your bucket, hopefully carrying the oil with it. As you might imagine, you can get seriously hurt doing it if you're not careful.

    Cold skimming involves opening the tapping and adding feed water at just a trickle, so the surface water slowly dribbles out into your bucket, hopefully carrying the oil with it. You can leave it going for hours. Make sure the boiler is switched off.

    New boilers need to be skimmed because oil gets into the system from cutting and assembling the new pipes.
  • Brad White_203
    Brad White_203 Member Posts: 506
    Great Gush

    I prefer to think of skimming as the gentlest overflow above the waterline, carrying what floats away with little turbulence. Usually done hot but always sub-boiling.

    The visual I have is that overflow pipe in that sink behind the ice cream counter where they dip the scoops between Chunky Monkey and Butter Pecan.

    My $0.02

    Yours in Cherry Garcia,

    Brad
  • David Nadle
    David Nadle Member Posts: 624
    Brad's right of course

    Let's just say the guys that hot skimmed my boiler after installation were doing it wrong.

    I guess you bring the water to 200 or so to reduce the viscosity of the oil but why? It seems to me a higher viscosity would help the oil "grab" the water as it flows out.

    All that ice cream and you are looking at the overflow pipe...



  • Brad White_203
    Brad White_203 Member Posts: 506
    Drain Pipe in an Ice Cream Shop

    LOL, David! Thanks. I needed that..

    Had to do something while waiting... I already scoped out the air diffusers and radiators so moved on to plumbing. Figures... :)
  • another good boiler

    Another good boiler piped wrong... time to get a REAL steam boiler pro. If you look into the boiler manuel, you'll see the pipings isn't the way its shown as per required layout.


  • Tim-
    Scroll back through the answers to your questions and find one by Gerry Gill. (LOL- It is the one below this! )
    Click on the red lettering under his post and it will take you to a site with a couple of pictures of work Gerry has done. Study carefully the header setups (size, design etc.in the pictures. He does cherry work!!!

    Reading Dan's book "The Lost Art of Steam Heating" and studying the pictures of systems which the steam guys on here have done has really helped me work out the problems with my own system and has saved me a bungle. The book teaches you the theory and the pictures show you how it is applied.

    If it was my furnace, I'd take a careful look at the design, sizing and layout of the piping coming out of the furnace. I've learned there was a lot more to it than just hooking up "A" to "B". You may want to find a good steam man and ask for his recommendations.
  • Tim_64
    Tim_64 Member Posts: 76
    Actually

    Actually the system is starting to run very well with fine tuning of venting, and finally getting clean water out of all the mains and new boiler.. (see pics)

    In all it take 35 minutes to satisfy a 5 deg call for heat

    http://forums.invision.net/Thread.cfm?CFApp=2&Thread_ID=59547&mc=6

    Perhaps when I correct the near boiler piping that I rushed to install (back against the wall with heating season upon us) My system will be able to satisfy a 5 deg call for heat a few minutes more quickly.

    Currently the hissing and spitting is almost gone. I guess diligent cleaning and assuring pitch of rads is correct,and all other variables are considered really matter. I still want too get the pressure down, and will attack that task promptly.

    Of course I could have hired a REAL pro and had this install done. But my cheap inner geek and the ability to get the packaged boiler for cost ;-) (less than 2 large) I managed to save myself a tidy sum of money!

    Kudos to all that have offered advice

    For those that offer nothing... please grow up. There are to many more important things to deal with in the world than keyboard warriors...