triple aquastat

paul_91
Member Posts: 62
can anyone explain to me how a triple aquastat operates with other circulators , using ra845a relays?....confused..
0
Comments
-
Are you maintaining Boiler temperature? If you are connect you others as if it's not there. If your only firing the boiler on a call for heat then take the circulator out of the triple and use a multi zone control or seperate controls with end switches wired back to the T T of the triple. Option 2 use zone valves and one circulator off the Triple aquastat with the end switched to the T T.
Note: If you don't want to maintain boiler temperature disconect the blue wire from the terminal inside the triple aquastat.
0 -
not sure that this is what you want
but it oughta be of some use. See page 8
0