Hello, I have a little bit of side walk I installed some tubing in at our office. When it comes to heat exchangers, I'm a bit of a novice. I have bought those small flat plate units in the paste from small baseboard zones (off of a water heater), and the local suppliers claims they're rated for 100,000 btu, or something like that. Seems hard to believe (that's why I'm the novice). So, my side walk is 50' x 5' wide, and two small returns to the doors at about 3 1/2' x 7'. I have 5/8" tube 8" cc. Thanks for any thoughts, Gary
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=368&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=368&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
So about
299 square feet of area? If so I'd go with at least 150 btu/ square feet. or about 44,850 BTU required. For heavy snow areas or faster response consider 175 btu/ sq. ft. I've seen designs at 200 for critical public access ramps, etc.
The HX would be sized based on the BTU load type and % of fluid, and the operating temperatures on A and B side, etc, etc.
Have a heat exchanger rep help you with sizing. Plenty of exchange in those small bricks
hrBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
thanks hr, I'll see if I can get more info. The local supplier usually says "it'll work" with no numbers.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements