Heat antisipator setting

what plumb said. Complete the circuit at the T'stat with the ten loops wrapped around your clamp on and run the unit,divide the reading by 10 and set your anticipator to that number. He's smarter than me though, I just clip two regular store bought alligator leads together to make one long enough to go around ten times. I like his homemade version idea. Can't understand why I never thought of that. ;)

Comments

  • Mike in NH
    Mike in NH Member Posts: 1
    Heat antisipator setting

    I have a Honeywell triple aquastat relay Type L8124A,C,J..

    What should be the heat antisipator setting?

    Thanks
  • martin
    martin Member Posts: 144
    anticipator setting

    Some controls tell setting on lid, but I always measure with a clamp type amprobe. I have a piece of therm wire with alligator clips and 10 loops take your reading with clamp on all 10 loops and devide by 10