flow rates for radiant

ed m
Member Posts: 65
trying to see what to set my flow rates on manifold, 5 loops 1/2 pex at approx. 250ft per loop. for radiant in floor heat off an indirect.
thanks
eddie
thanks
eddie
0
Comments
-
Some variables need to be nailed down.
Hi Eddie,
It all starts with your heat loss (of course!), but also your floor covering R-value and net radiant area. Also, is it a slab, sub-floor panels, what now?
A short answer would say that 0.5 to 0.75 GPM per circuit is a reasonable flow rate range, but what temperature drop?
Some designers prefer a 10 degree temperature drop to reduce temperature contrast, some go 20 and have no issues.
By the basis I give above, you could supply between 18,750 and 37,500 BTUH and if a maximum density of 30 BTUH per SF, 625 to 1,250 SF of radiated floor area.
Too much of a range to give you the real answer which is probably something else...0 -
Hey Eddie,
Here is a Radiant Panel Worksheet I made for this purpose.
Might help you..0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 67 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements