flow rates for radiant

ed m
ed m Member Posts: 65
trying to see what to set my flow rates on manifold, 5 loops 1/2 pex at approx. 250ft per loop. for radiant in floor heat off an indirect.
thanks
eddie

Comments

  • Brad White_201
    Brad White_201 Member Posts: 52
    Some variables need to be nailed down.

    Hi Eddie,

    It all starts with your heat loss (of course!), but also your floor covering R-value and net radiant area. Also, is it a slab, sub-floor panels, what now?

    A short answer would say that 0.5 to 0.75 GPM per circuit is a reasonable flow rate range, but what temperature drop?

    Some designers prefer a 10 degree temperature drop to reduce temperature contrast, some go 20 and have no issues.

    By the basis I give above, you could supply between 18,750 and 37,500 BTUH and if a maximum density of 30 BTUH per SF, 625 to 1,250 SF of radiated floor area.

    Too much of a range to give you the real answer which is probably something else...
  • Josh_10
    Josh_10 Member Posts: 787


    Hey Eddie,

    Here is a Radiant Panel Worksheet I made for this purpose.

    Might help you..