Time was when most circulators were installed on the return side of boilers, the reasoning being that the circulator would see lower water temperatures and last longer for it.
An outfall of that thinking was air removal. The air scoop was placed at the outlet of the boiler where the water was naturally hottest and thus allowed to release most of it's entrained air.
The downside was, there was a neat little tapping there for the expansion tank. Not bad in and of itself, but then it was <i>used</i> to connect the expansion tank. Now you were "pumping to" rather than "pumping away" from the expansion tank.
That is the most important thing you can do. If you do not move the circulator, move the tank connection point to just upstream of the circulator.
An outfall of that thinking was air removal. The air scoop was placed at the outlet of the boiler where the water was naturally hottest and thus allowed to release most of it's entrained air.
The downside was, there was a neat little tapping there for the expansion tank. Not bad in and of itself, but then it was <i>used</i> to connect the expansion tank. Now you were "pumping to" rather than "pumping away" from the expansion tank.
That is the most important thing you can do. If you do not move the circulator, move the tank connection point to just upstream of the circulator.
0
Comments
-
Circulating pumps
I've been told that the circulating pumps for my hot radiators should push the water thru a boiler rather than pulling it thru any body know ??0 -
Hey Brad, thanks for the info just to let you know the way my system is set up, I have the expansion tank on the return side of the boiler then on the feed side I have the pump, so I should move the pump so it can push the water thru the expansion tank and then the boiler - yes ????0 -
In this order
Boiler out-expansion tank-circulator0 -
As Joe said. Pump
Away from the expansion tank, always, no matter what side of the boiler it is on.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements