reverse
Big Ed_4
Member Posts: 3,090
The reverse auastat will switch on with temperture rise. Itst primary use on a boiler is it only allows the circulator to come on when the boiler is hot enough to help prevent combustion condencing. And it the boiler supplies hot water though a coil, it shuts of the circulators on temperture drop to prevent loss of hot water.
The triple has two high limits , a reverse and a switching relay to control the circulator from a thermostat. When the thermostat is not calling , the low controls the boiler water temperture for hot water or just to maintain mininal boiler water. With a call for heat from the thermostat , the burner will fire up and the circulator will run. , The circulator may cycle on and off. This depends on returning water from radiation. The burner will run until temperture reaches the High plus the( Diff - 5*)
The triple has two high limits , a reverse and a switching relay to control the circulator from a thermostat. When the thermostat is not calling , the low controls the boiler water temperture for hot water or just to maintain mininal boiler water. With a call for heat from the thermostat , the burner will fire up and the circulator will run. , The circulator may cycle on and off. This depends on returning water from radiation. The burner will run until temperture reaches the High plus the( Diff - 5*)
There was an error rendering this rich post.
0
Comments
-
reverse
can somone explain what reverse aquastat does....and is it the same as a triple aquastat?0 -
thanks
thanks great info...0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements