GLYCOL
hot_rod
Member Posts: 23,167
typically only Di-potassium phosphate is added to RV fluids.
This is not enough protection for modern hydronic systems. RV fluid is intended to be flushed out after use, so a comprehensive inhibitor package is not required. The price reflects that, of course and there are different blends offering different freeze and burst protection levels.
hr
This is not enough protection for modern hydronic systems. RV fluid is intended to be flushed out after use, so a comprehensive inhibitor package is not required. The price reflects that, of course and there are different blends offering different freeze and burst protection levels.
hr
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream
trainer for Caleffi NA
Living the hydronic dream
0
Comments
-
hAVE A WEIL-MCLAIN GAS BOILER m/nPG5-FPDN SERIES 2 CAN I USE PROPOLEYNE GLYCOL IN THE SYSTEM. ANY PROBLEMS WITH PUSH NIPPLES0 -
probably
check with the Weil installation manual, they usually address that.
Be sure it is a glycol inhibited for hydronic use. Stay away from RV type of fluids
hrBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
RV type glycol
Would you explain, HR, once more why not to use RV type fluids. I had a homeowner wanting to pump 25 gallons into his self-installed system. One brand, on sale 2 for $7.00, is labeled "-50 burst protection" but only scales out at 15 degrees on my instrument. If I remember correctly, it will foam from the pump turbulence?0 -
thhe RV stuff...
is not rated to be use in heating systems. I t has no oxygen inhibitors and will break down pretty quick.0 -
Your instrurment...
(refractometer)is telling you the freeze protection number. That is the temp at which the very first ice crystal will begin to form and start turning it into slush. Then there is flow protection, which is the temp at which it will cease to flow as a slush. Burst protection is the number at which the solution will stop contracting and begin to expand again. All glycols will contract at first as the temp drops but below a certain temp will begin to expand. What you have in your can that starts to freeze at 15* is some mixture of glycol and water not 100% glycol. Generally you can only find the 100% stuff at the higher latitudes where extreme cold can be experienced. You have to special order it in most of the lower 40 states. It always pays to check what's in the can with your instrument before adding water because, as you have discovered, it could already be at the freeze temp desired straight out of the can and adding water will dilute it further and cause you many woes, whether it be removing and adding more because you checked it afterwards and it was weak or failure of your system because you didn't check it and found out the hard way. The -50* burst protection advertised throws a lot of people off the track and sells a lot more glycol for the mfg when you have to throw away part of what's in the system and then buy and add more. I personally have a real bug up my butt over that.0 -
Also
Automotive AF has silicates, finely ground sand, which I am told assist coating the passages and do other useful things in a car. But in a hydronic system, become an abrasive slurry. Never mind the chemistry.
Check out Noble No-Burst. Drew at Noble has always been very helpful.0 -
PG
MPF
I couldn't of said it better. Just 1 note: We have a couple of products that are 98%(Super Noburst) & 96% (Noburst HD). These are diluted by the contractor to a desired freeze Temp.0 -
Thanks,
I'll keep those products in mind if I move forward with the one I have on the table right now.
m0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements