Thermal trap
Roland_14
Member Posts: 10
Hi All,
I have a 30Gallon Super-Stor indirect which is exhibiting hot water creeping up the cold water feed pipe. I have heard of being able to pipe a simple thermal trap to prevent this but I can't find a good picture to illustrate how to do this. Do any of you fine gentlemen (and ladies) have a picture or a link which shows a detail of this device?
TIA, Roland.....
I have a 30Gallon Super-Stor indirect which is exhibiting hot water creeping up the cold water feed pipe. I have heard of being able to pipe a simple thermal trap to prevent this but I can't find a good picture to illustrate how to do this. Do any of you fine gentlemen (and ladies) have a picture or a link which shows a detail of this device?
TIA, Roland.....
0
Comments
-
Before your cold water supply line enters the side of the inlet, drop your pipe 30 inches below the inlet then two elbows and come back up and tie into the inlet.0 -
27 \" piping trap
check the holby website for piping diagrams. simple heat sink drop down 27 " on the vertical.& back up use a check valve & ex. tank0 -
We go off top of tank and desired height, make a u turn and drop hot pipe down at least 12", we do 18" and then go back up to original hot pipe.0 -
to clarify
i meant one or the other ----not both0 -
Thermal trap
Before tying in to the inlet or right after coming out of the outlet of said apparatus you drop down with the piping,I usually go 12", then go straight up and continue with your piping.0 -
Thermal Trap
Thanks to all who replied to my question.
Bob Young; I cannot seem to find the information/diagrams on the Holby site. Do you have a link?
The Super-Stor Ultra has the cold/hot fittings on the side of the tank with the cold near the bottom. I'll post a picture.
FYI The cold in/ hot out fittings are on the left of the tank.0 -
Click here: Home Page
this should work : Click here: Home Page0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements