lose the wet return?

Timco
Timco Member Posts: 3,040
It would seem that is a better option than busting up the floors in several basement units, no? what is typically done with these old buildings when the wet returns all rot out?

Tim
Just a guy running some pipes.

Comments

  • Timco
    Timco Member Posts: 3,040


    My newest account is talking about the possibility of ditching the wet return due to the condition of just 4' of pipe I pulled last week. This would mean that all returns would be intercepted and ran back to boiler room as a wet/dry ret and a condensate tank added? Building is u shaped, 100+ yrs old, and boiler is almost at far end of the u. 32 units, 3-4 stories high...where to begin an estimate on this? Anyone want to add the cost of a plane ticket to engineer something of this scale? All well into the winter / spring at this point, but I want to play serious...


    Tim
    Just a guy running some pipes.
  • gerry gill
    gerry gill Member Posts: 3,078
    anyone who would

    change wet returns for a condensate tank is an idiot and maybe the building owner and the condensate tank deserve each other..

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • Can all the condensate

    drain back to the boiler if you run the pipes as dry returns ? Can they be run on top of the basement floor ? I'm not a fan of condensate pumps unless they're absolutely needed - like remote areas where the condensate won't travel back by gravity .
  • bob young
    bob young Member Posts: 2,177
    condenate tank, not

    WE usually run them exposed along perimeter of room. box in if necessary. run in copper. easy , lucrative project.
  • Timco
    Timco Member Posts: 3,040


    would you be willing to email me direct and talk price? Any ballpark would help...

    Tim
    Just a guy running some pipes.
  • Steamhead (in transit)
    Steamhead (in transit) Member Posts: 6,688
    Stay with gravity return

    Adding a tank and pump, and all the traps you'll need to make it work, can become a servicing nightmare. There would just be too many moving parts. The Dead Men designed that system to work with gravity return- no need to change that.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    wet return resleeve

    is it possible the underfloor piping is large enough [and straight enough] to shove a thinwalled flexible copper line through with connections for the dry returns?--nbc