Flush valve
Options
Jim Pompetti
Member Posts: 552
I had a idea how to save a little money on an steam install. On the bottom of the boiler , we install a flush valve to (of course) flush the bottom of the boiler during cleaning. By using a 2 1/2 inch nipple, an ecentric reductor and either a 1 1/2 " or 2" ball valve we can save about a $100. Do you think in will hinder the flushing.
0
Comments
-
Velocity
Assuming a cold flush, if you can get an inflow of 19 GPM for a 1-1/4" full-port valve or 26 GPM for a 1-1/2" full-port valve, I would think that you could carry away any loose silt.
I would think that at least 4 FPS is essential, 6 FPS if you can. That means a lot of water though and possibly the ability to valve off all other ports to keep the pressure up. Do watch that pressure of course, I know you will.
More flow (if you can get even those flows to begin with), should not hurt. The way I figure it, if that velocity will not carry the mud away, it was not meant to be
Naturally you are up against a reasonable flow rate and velocity, but not having a valve so small that it will clog. I like that you are using eccentric reducers. I cannot always find them locally but have a couple I salvaged.
If you are doing a hot operating blow-down, naturally that will limit your make-up rate.
My $0.02 anyway.
Brad0 -
Brad
I think you are in the Philly area , Betzs Supply , in Lester Pa ,carries ecentric fittings and can ship them to you.0 -
Hi Jim!
Actually, I am in Boston. I do not do a lot of installation work, but when you need them, you need them badly
Nice old cast iron fittings are hard to find. Our old gravity HW system fittings will find a new home in a steam system at some point. Re-use, recycle!
Peace.
Brad0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements