1-inch minimum for the runout, and I'd pitch it down and vent and drip the end. Run the drip back to a wet return. Going counterflow here may produce banging unless you could get some serious backward pitch!
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
Pipe size for steam
I'm looking at adding a 6 foot section of cast iron baseboard. The pipe run will be 24 feet. Is that to long for 3/4 pipe?
Thank you
Mark0 -
It looks like I can get about a 4" drop in 20 feet. If I go with an 1-1/4 or 1-1/2 pipe and use a 3/4 riser up through the floor. Do you think that will work. Or will I just be making problems for myself.0 -
is this for steam or hot water0 -
2 way street
Can you construct a 2 way street just 12' wide?
will traffic flow safely and smoothly both ways?0
This discussion has been closed.
Categories
- All Categories
- 86.8K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 425 Carbon Monoxide Awareness
- 109 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 966 Plumbing
- 6.3K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements