trying to estimate savings...
Timco
Member Posts: 3,040
Very even heat, I have not inspected the mains. Boiler is controled by a t-stat in the middle hall area top floor so it is always on. I turned pressure back to 1.5# from 8 or so. Boiler is in far end of U shaped complex.
Tim
Tim
Just a guy running some pipes.
0
Comments
-
One pipe steam, 32 units, average unit is 500 sq'. Average temp is now 84* because most valves do not close, and no TRV's. Some have 89* areas. Many windows open. How would I calculate savings with TRVs? Gas bill is $2400 average cold months, high of $3600 last winter.
Thanks, TimJust a guy running some pipes.0 -
TRVs would help
but I'd say the building has other issues....
How do they control the boiler?
What pressure are they running?
Are the mains properly vented?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
First thing I'd propose
is an outdoor control such as a Tekmar #279.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
That is a good suggestion...but how do I throw out a possible savings number for the control & TRVs?
TimJust a guy running some pipes.0 -
What I would tell them is, you are spending upwards of
$25,000 a year and building is too hot, I can't say exactly what % you will save but you will get a savings just in not opening windows with the Tekmar control. I would also lower operating pressure if feasible and see how system responds to it. Also check main vents to make sure they are operating right as steamhead mentioned. I am sure there is an appx way of calculating savings but I think if you just show owner all windows open maybe on a video clip and photo shop dollar signs coming out the window that he will basically get the concept. Good luck0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements