sizing pex home runs to radiators
I would like to run 3/8 pex home runs to a mix of ci and panel rads. the largest of which is 7500 btu's . Am I making a mistake not running 1/2.0 -
I run 2-pipe zones all in 3/4 to CI rads.
TimJust a guy running some pipes.0 -
Unless it is a rediculous long run, I don't see why 3/8" wouldn't work in your application as the rad requires less than 1 GPM.
Save your money on the larger PEX0 -
I use 5/8\" Pex-Al-Pex
and not just to be different...
The OD is the same as 3/4" copper so is easy to support with clips. Holds it's shape and the flow characteristics are wide enough to handle the smallest to the largest radiators. I even have served two large radiators via a 1.25" old gravity riser from a single 5/8" circuit.
Everyone has choices.0 -
3/ 8 or 1/2
would carry ,75 gpm easily. 100 feet of 3/8 flowing .75 gpm of 160F water would have a pressure drop of 8.5 feet of head. easily within reach of a typical 80 w circ.
At a 35 degree delta T in the circuit, common in Europe, you could move 15,000 BTU/ hr @ 10.7 feet of head pressure drop.
Consider TRV's and a delta P circ for the best efficiency on the distribution side.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
and PEX-AL-PEX to reduce noise issues!
It's pretty rare to need more than 1/2" pipe for any single, dedicated radiator.0 -
Nothing pulls or handles quite as nice a 3/8. Two pipes pull smoothly through a 1.125 inch hole.
Noise is not much of an issue in constant circulation systems. Temperature changes are gradual and don't cause the rapid expansion noises that can occur in on/off regulated systems. Full reset constant circ. also makes me more comfortable with the possibility of long term pex chaffing issues.
I'm doing a 3/8" home run panel radiator job right now. On some of my shorter runs I'm extending my return leg a bit and doing extruded plates for a little bonus radiant in selected areas.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements